Was asked by my local landlord to have a look at his new fryer as its tripping the 32A mcb.
Its cabled from cu to cooker switch via 6mm t&e and then to fryer in 2x 4mm t&e.
Further investigation reveals the appliance has 2 x 12kW seperate fryers with a total load of 63A! so no wonder it trips the mcb when both fryers are switched on together. Taking diversity into account it will still require almost 22kW
The cu (one of many in the premises) is protected by a 63A / 30mA rcd main switch which feeds 4 x 32A rings, 2x 20A radials and 3 x 6A lights so I doubt if he can add a 63A supply from here!
My advice is to request a further supply from dno and feed the fryer direct from its own db.
Has anyone any experience of theseheavy duty fat fryers?
Any comments on the best way to proceed.