PIR today on a shop premises.
All okay, except one of the CU's is faulty.
It's an old metal wylex, originally with rewireables, but it's been upgraded with plug in MCB's.
The trouble is, the main black moulding has cracked, so one of the screw on insulators (the bit the fuses or mcb's plug into) has nothing to screw into. So if you unplug that particular MCB, there's nothing to stop the insulator coming out and exposing live terminals.
I think it should be a code 1 and recommend a CU change. Do you agree?
Also for a CU change, being commercial, all wired in conduit or surface, an I correct in saying there's no need for an RCD?
I probably would fit a new single RCD board anyway (only 4 circuits), just curious about it. Having PIR'd it, I know there are no issues with IR or anything else that would upset an RCD.