OK,
Curious, why does the earth wire need increasing in size?
Curious, why does the earth wire need increasing in size?
I never said that. It seemed as if curious-one had a reasonable idea what he was doing but as he is quite happy to leave the installation in a dangerous state it shows that he hasn't.Ok, so you think that nobody should be allowed to do any DIY electrical work,
One DIYer patting the other on the back for leaving a potentially dangerous installation powered up.well, curious one is entitled to do what he likes, as am i, and as is Apache.......
Full marks curious one i say...
in TT systems, the max fault current will be L-NSorry sidewinder I missed your post in the mass of others. My incoming supply is 60A at 235v, but from what I gather I need to know Ra to calculate the maximum fault current, which it seems I do not having due to the earth not being correctly tested. The largest circuit that is available at the moment is the cooker at 30A (obviously off as stated earlier) but there will be a requirement in the near future for a 40A shower. The fuse board will be upgraded to a CU (by an electrician, I don't have the tools) which will be 30ma rcd and rcbo protected circuits. If I don't need Ra then if someone can link me to the calcs I'll do them immediately, thanks.
Sorry just read further, the old cable is chased into the wall and then exits at the bottom.