I am confused with calculation of Zs. Using the formula Zs=Ze+(R1+R2) then a typical value for a type C 32A mcb to BS EN60898
would be 0.8ohms.For a TN-S supply then Zs=0.8+(R1+R2) so whatever the values of R1+R2 surely the installation will not comply?
Thanks in anticipation for any input. This is kind of work related. I work in luxury motorboat industry and we are having to come up
with a testing procedure(2x 3phase generators and 3phase shore supply with isolation transformer)
Thanks guys