Hi,I was observing/moithering a qualified experienced spark do a consumer change and got some questions to ask on the way he tested things (didn
hammer4) Upstairs lighting all the ceiling roses were painted over and nigh on impossible to remove the covers, any tips for removing theese.
It does actually depend upon how the lights are wired, looped at fitting or looped at switch. A switch could have a longer earth path (R2), but because the power has got to get back to the light fitting the light will have the longer R1. As a general rule the fitting is the preferred place. though I can understand if the fitting is inaccessible or would cause damage to the decoration it may not be practical. As such a limitation may need to be noted and get your reading as near as possible.HiRe: This wouldn't give you R1 + R2, so what's the point in measuring it.
No need for R1 + R2 anyway, but 'Continuity of CPC' needs to be confirmed at furtherest point on each circuit and other relevant points. (e.g. metal switch plates & other exposed conductive parts).
It is acceptable to use Zs test to confirm continuity.
Can i ask why this wouldnt be R1+R2? in the books i have read and college, to test at all points including light switches the highest value would be R1+R2 for that circuit and sould be the furthest point, wouldnt the switch be the furthest?
:C or am i getting summat wrong??(most likely)
5) Insulation resistance on the ring was done by connecting the 2 lines and 2 neutral together and testing to earth is OK on a CU change?
That's OK, but why was he IR testing individual circuits.
Only requirement is 'full board' IR test with L & N connected together and tested to earth.I
which if not done before cu change will cause big problemsOnly doing full board IR test is not strickly correct. As if low readings are found, individual circuits need to be tested anyway. In which case testing individually whist swapping circuits onto a new CU is not a problem. It could also be more helpful to assist checking for circuits sharing a common neutral, preventing "borrowed neutral" problems.Doc H.
you have to be careful of not damaging the customers decoration and some older roses could be brittle and break if you try forcing them open. Who pays if you mess up the lounge ceiling. Some of those plug in light adapters can allow you to get some readings onto the case of a fitting if it is metal. Also with some Class 2 fittings you may struggle to get an earth anyway.4) Upstairs lighting all the ceiling roses were painted over and nigh on impossible to remove the covers, any tips for removing thees.
R1 + R2 is only a requirement during 'Initial Verification' - i.e. new installation, as this is the only time you can get a true reading of the resistance of R1....Line conductor and R2....CPCHiRe: This wouldn't give you R1 + R2, so what's the point in measuring it.
No need for R1 + R2 anyway, but 'Continuity of CPC' needs to be confirmed at furtherest point on each circuit and other relevant points. (e.g. metal switch plates & other exposed conductive parts).
It is acceptable to use Zs test to confirm continuity.
Can i ask why this wouldnt be R1+R2? in the books i have read and college, to test at all points including light switches the highest value would be R1+R2 for that circuit and sould be the furthest point, wouldnt the switch be the furthest?
:C or am i getting summat wrong??(most likely)
From the ESC Best Practise Guide:I know I may be pushing my luck a bit but is there any chance someone could list down the minimum/quickest tests when doing a board change as when I'm doing them I'm doing full testing ie initial verification. Sorry to butt in on your thread btw. Cheers
Do this with a wander lead, like I said.So that it why its a good idea to test all metal light fittings not test at the switches.
ehhh??? ?:|R1 + R2 is only a requirement during 'Initial Verification' - i.e. new installation, as this is the only time you can get a true reading of the resistance of R1....Line conductor and R2....CPCDoing R1 + R2 on a board change or a 'Periodic' is pointless because of the possibility of parallel paths.
If you look at Supplementary Bonding of a bathroom - the R1 + R2 measurement of a circuit would be measured before this bonding was installed because all earths, exposed conductive parts and extraneous conductive parts are then bonded together - giving a multitude of parallel paths which, in turn, would give false R1 + R2 readings - so what's the point in taking them.
You have to remember what you are actually confirming whilst aquiring your R1 + R2 - it is the continuity of protective conductors - the R1 + R2 measurement is a bi-product (and not even mentioned in the Regs)
Measuring Zs on a 'Periodic' or 'Board Change' is just as effective, with wander lead tests to 'Exposed Conductive Parts'.
Equally effective methods include (R1+R2)+ZeWhere protective measures are used which require knowledge of earth loop impedance, the relevant impedance should be measured, OR determined by an equally effective method