Converting consumer unit to duel.

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

John Stone

New member
Joined
Sep 23, 2024
Messages
3
Reaction score
0
There is an oldish metal consumer unit with a 100 ma RCD and 10 MK MCBs all in very good condition, I want to convert it into a duel unit with two 30ma RCDs and double pole main switch, There are a couple of spare ways in the unit and if I remove the 100ma RCD there will be room for the new RCDs but I would then need to place a main switch in a separate small unit next the the existing one and wondered if there is any reason I can't do this.
 
The box will save you around £40, and you will find it difficult to get all the new bits in, if you can find all the parts you need like neutral and earth bars, plus the mounting brackets for the. Buy a new board and save yourself a lot of swearing 😀
 
Top