The 3036 board is protected by an upfront 30ma rcd and there are 3 free ways in the board. Also i cant see anything wrong with using the existing 3036's, I would have split the tails and put in small a consumer if there were any problems, for example no rcd protection.

Cheers

 
soulman, rip that carp old board out, and replace it with a nice shiney new 1, the install will be alot safer. and youll sleep at night knowinfg the installation meets regs.

 
Yep ! As far as I know as long as you achieve Disc.Times and add an RCD somewhere I think you could still go with a 3036 board. Highly unlikely though. Customer a couple of years back told the builder he wanted a BS3036 board fitting as thats what we have on the Railways . No intention of fitting one as it wanted to be a split load anyway but made the enquiry at the wholesalers.... no...could'nt source one anywhere.
Here you go, Wylex Standard Series Consumer Units from Shop4 Electrical No excuses now !

 
Last edited by a moderator:
hi, ChapsI need to install a cooker 3.2kw & a hob 6.0kw. I was going to install the hob on 6mm 30a 3036 fuse and install the hob on 2.5mm and a 15a 3036 fuse to feed a 20a d.p switch or 13a fcu.

Someone suggested to use the 6mm cable 30a 3036 fuse to feed both using a unswitched f.c.u for the hob

any advice appreciated
Spot the problem

 
The retrofit MCBs for old wylex boards are 60898s with 3kA breaking capacity

The 3036 board is protected by an upfront 30ma rcd and there are 3 free ways in the board. Also i cant see anything wrong with using the existing 3036's, I would have split the tails and put in small a consumer if there were any problems, for example no rcd protection.Cheers
I'd push for a new board as one RCD is not ideal.

I'd also use a retrofit 32A MCB if client didn't want an upgrade.

 
Dual accessory box, cooker outlet plate and unswitched fused spur......jobs a gud un!
No i would put a switched fused spur next to the cooker switch for the cooker connected to a cooker outlet so you dont have to pull the cooker out to change the fuse.

 