Howdy guys
doing a C/U change at a job where 3 lightin ccts have bad readings 1./ dead short (original fuse blown) obviously not re-connecting that one, 2/3./ have .21 and .4 IR readings. The house is unoccupied and pretty mouse infested at the moment.
Obviously strongly recommending full PIR/poss part whole rewire.
I've re-connected (temp only) ccts 2/3 and the RCD's don't trip
There is also a 6mm G/Y to rthe airing cupboard bonding some pipework.
I've put in 10mm to services etc should I leave out the 6mm or put it back in
Owner arrives back mid Dec and he wants to stay in his house for a few weeks before heading back to Brazil. Going by the "changing CU doc" i just have to inform him of any non-compliant circuits that I've re- connected.
Rambled on again, but potentially loads of good work here
any advice?