hello.
thoughts please....
today we have 2nd fixed a lighting circuit. all ok until we connected the 4 way switches... and suddenly 230V goes down earth...
any way one of the 3 cores has a dead short on it about 0.45ohms. me thinks a screw.
property has been plastered and painting and they don't want any more mess.
now.... i have explained we need to replace the cable or find exactly where the fault is and join extend ect.
but if i disconnect the earth from both ends and put them in a block. this then means that cable will have no earth.
but at every point there is a contuinous path to earth from switches and fittings.
so there for what would you do.... ????
i know the best thing would be to replace the cable but you know how it is
thoughts please....