There's been quite a bit of discussion recently regarding CU changes and the paperwork involved.
It was pretty much settled that if you're not doing a PIR on the existing installation, then you issue an EIC with accompanying schedules for the CU install and connected circuits.
So, I have a question.
You're doing a CU swap in a domestic.
If the customer asks for an existing single-socket radial not to be put on an RCD (say, for an aquarium), what do you do?
We know that in the 17th you can have a dedicated, labelled socket outlet without RCD protection but......the cable feeding this socket is unlikely to be buried deeper than 50mm, nor is it likely to have mechanical protection.
The Regs say this cable should have 30 mA RCD protection and you're not allowed non-compliance on your EIC, but you also don't have to bring an existing installation up to 17th spec - so do you do as asked?
You also have to consider this guidance from the ESC best practise guide -
5.4. Where a consumer unit is being replaced, additional
protection by means of RCDs in accordance with Regulation 415.1 should be provided to the extent required by the current edition BS 7671, such as for:
It was pretty much settled that if you're not doing a PIR on the existing installation, then you issue an EIC with accompanying schedules for the CU install and connected circuits.
So, I have a question.
You're doing a CU swap in a domestic.
If the customer asks for an existing single-socket radial not to be put on an RCD (say, for an aquarium), what do you do?
We know that in the 17th you can have a dedicated, labelled socket outlet without RCD protection but......the cable feeding this socket is unlikely to be buried deeper than 50mm, nor is it likely to have mechanical protection.
The Regs say this cable should have 30 mA RCD protection and you're not allowed non-compliance on your EIC, but you also don't have to bring an existing installation up to 17th spec - so do you do as asked?
You also have to consider this guidance from the ESC best practise guide -
5.4. Where a consumer unit is being replaced, additional
protection by means of RCDs in accordance with Regulation 415.1 should be provided to the extent required by the current edition BS 7671, such as for: