I looked at a job recently where a distribution circuit was feeding a 3ph dist board some 10m away.
My concern is that the only protection for the cable is by the DNO fuses (Labelled at 1361 100A - sealed so unable to confirm)
Cable is 16sq 4c clipped direct and rated at 94A (Table 4E4A - BS 7671) - Therefore not meeting requirements of Overcurrent protection for the cable (although very close)
The DNO have installed their own isolator (3pole switch) and a rotary isolator (3p) has been installed by a previous sparks
as further isolation. (Unable to ascertain current rating of rotary but that is another issue)
Anyone come across this issue before and how did you resolve it? Cheapest way I can see is to get DNO to derate fuses to 60A still would provide enough for end user.
My concern is that the only protection for the cable is by the DNO fuses (Labelled at 1361 100A - sealed so unable to confirm)
Cable is 16sq 4c clipped direct and rated at 94A (Table 4E4A - BS 7671) - Therefore not meeting requirements of Overcurrent protection for the cable (although very close)
The DNO have installed their own isolator (3pole switch) and a rotary isolator (3p) has been installed by a previous sparks
as further isolation. (Unable to ascertain current rating of rotary but that is another issue)
Anyone come across this issue before and how did you resolve it? Cheapest way I can see is to get DNO to derate fuses to 60A still would provide enough for end user.