just a quick suggestion on mine i have ct clamps settings as pv not grid if i select grid it stops coms to meter but PV setting allows meter to comms
Mine has a meter select tab where i chose single phase meter. Also a separate CT install tab with a choice of grid or PVjust a quick suggestion on mine i have ct clamps settings as pv not grid if i select grid it stops coms to meter but PV setting allows meter to comms
choose pvMine has a meter select tab where i chose single phase meter. Also a separate CT install tab with a choice of grid or PV
Perhaps listing the parameters would help?Can someone help me with a few settings or the settings list of what they should be please
Time of use is for charging from the grid or feeding back if you are getting paid. For instance, If you have an economy 7 account you may wish to charge the battery overnight so that you can use that power during the day when the cost from the grid is higher.The power rate setting I'm. Not sure is that what the unit will. Supply. To the house from export
And the time of use stop or run not sure what that would be
Plus charge times I gather that is charging the batteries when they get low charge from grid not export, when our microinverters are exporting do I need to. Go. To. Specific setting to tell inverter to charge the batteries or does it just automatically know this export use
Yeah, I saw on youtube that setting to zero is not recommended.I've seen something similar to this before.
We had an inverter not charge over 24% then after some messing about we had no charge to battery. After many calls to solis we found the hybrid solis range all have a bug in the firmware which causes charging anomalies when export is set to zero and grid charging off. There is not a fix currently available I was told they are looking to add it into a future version. The way we resolved it was to allow 100w of export.
Not sure if this is indeed your issue but hope it may help in some way.
Just out of interest. What temperature is your inverter showing from the battery?What voltage do you have?
Ah, thanks for that. Deffo an issue with battery temp reporting. I've not seen an option to see the inverter temp.My v is 50.2v. and battery temp is 6.4 Deg. Inverter 19.5 deg
Thanks for your reply.Has anything changed. Have you checked the one rooms between the battery and inverter. Is the comuni action lead ok?
Just run through what's happening again