my take on this is regarding rin mains when installed correctly you would 2 earth paths and to conductor paths under fault current and over load, because you have 2 cables to the cu and 2 cables to each socket, therefore you have double the 27 amps capability ie 2 x 27 = 54
the size of the cable is 2.5 and you have 2 x those cables for the conctors therefore making 5 in total, and the earth is 2 x 1.5 making 3 in total, which would therefore allow easily 32 amps to pass through,
now with regards to spurring from a ring main i dont think it should be alowed as you only have one return path back to the supply through the ring main where it connects to, and so should be classed as a radial circut from the ring main, i think ring mains are pefectly safe when not spurred from, but spurring from a ring main is when it becomes a bit dodgy. and should be not done, thats my take on ring mains as for this problem of 2 radials being from one 32 amp breaker, then imho thats a big no no because there is only one earth path so the earth and current conductors cannot share the loading therefore the resistance will be higher, no if these were connected between the 2 ends of lines and made into a ring main, then no problem for those 2 items, my self id run them in 4 or 6mm though and have each appliance seperatly if it needs a combined 32 amp trip, or run each radial froma 20 amp mcb, job done all compliant