its protected against overoad & fault current, just like 7671 requires. therefore it is compliant.I would love to know what the weather is like on the planet you are living on if you think that complies. It does not. It's not a ring it's a radial end of story. Anyone who thinks otherwise really should get a copy of the brb the rest o us use (BS7671:2008).
The whole point is the cable is protected against overcurrent downstream. So with overcurrent taken care of then all we need to make sure is if there is a fault on the 2.5mm it will be cleared by the 32A rcbo. The bit about rings and spurs has a lot to do with the question as its permitted to have a cable that is protected against overcurrent downstream. Overcurrent can be dealt with in other ways not just at the origin of the circuit.OK. So, on the one hand, we have regular posts on here, which are NOT argued with, that the OCPD is protecting the cable, not the appliance.But Wozz`s OCPD isn`t.
Why is that such an issue? Sod the bit about rings & spurs - it bears no relation to the OPs question mate.
As has been said. IT DOES NOT COMPLY. (Unless you know of a "secret reg.", which is only in special copies of the BRB??? ] )
KME:C
Spot on I have also seen it on other topics. To just say it doesnt comply end of and not backing it up doesnt do anybody any favours. I suppose its easier to deny things could be right than try to understand logic.This discussion is going the same way as other discussions have in the past - i.e. I, (in my previous post), have detailed why it does comply by covering the protection required for the circuit and how it's achieved in this scenarithers then come on and post 'It doesn't comply'!!..........no explanation, no reg numbers, no reason for non-compliance......just shouting out their opinion.....it does your head inheadbang
I think the '3m' regulation must be being mis-read......Try reading all of the post. We posted regs at the start. Overcurrent protection has to be within 3m of the mcb and wozz still hasn't said it is within that therefore it's not apicable.
Then you have disregarded your only supporting reg. No others support you. It's a radial simple as and if you don't get that then maybe you should become a kitchen fitter!!!but that was disgarded as only a requirement for when a change occurs in CCC for 1 ocpd
And you are quite correct....... but as i said the circuit can be designed in many different ways i was just thinking about one that isnt the norm.
Not enough accessories and one spur per accessory (so only one spur at origin.Take a six-inch length of 2.5mm cable, strip the ends and then fold it in half. Connect both the stripped ends into the mcb. Voila - we now have a ring. It may not have any outlets, but it's still a ring. Connect the radial circuits into the mcb, as allowed (it is permissible to spur at the source) and the circuit complies. ] From a strictly "regulations" view, I'm with Wozz, Andy and others on this.
Would I do it myself? Probably not.
314.3 says needs to comply with ch43.Apparently, 314.3 applies, but I can't check what that is at the mo
Yes, if the RCBO was offering overload protection for our cables.314.3 says needs to comply with ch43.So 433,1,1(ii) seems to apply. The rated current or current setting of the protective device (In) does not exceed the lowest of the current carrying capacities (Iz) of any of the conductors od the circuit.
Well theres your nail. 32>27!!