What we need is special location to prove that in the event of a fault a single 2.5mm cable will trip the 32A rcbo, He could probably also tell the exact length that the 2.5mm could be and still operate the 32A rcbo in the event of the fault. Overload can be ommited as it has been provided further down the circuit by the 13A fused spurs/sockets. Dont think this will get through but worth one more try.Yours misses the point too.I do not think anyone is questioning if 13A fuse can protect a 2.5mm cable. The issue is actually that an unfused outlet for current-using equipment is not suitable for overload protection for the cable preceeding it. Wrong, the appliance has a plug on it with fuse fitted so a socket is never going to exceed 13 or 26A. The original post was regarding a fused spur so its not unfused is it?.
The other issue is the distance from the last change in current-carrying capacity (i.e. the MCB) needs ot be within 3m too if being used as fault protection. Wrong, This does not apply, you are providing fault protection for the cable, as long as you can prove the cable will operate the protective device(calc it) then length in this situation is not limited to 3m.