So I'd give then 6 out of 10 for actually using SWA.... (not T&E)...
but only 1 out of 10 for the method of extending the cable with an external joint half way up the garden by the fence....!
:shakehead
You can't see on the photo but all of the cores were nicked, probably with a knife, with the insulation cracked leaving visible copper conductor below.
My tests had shown a low IR and no continuity of the sheath..
following questioning, the customer then remembered a box about two thirds up the cable run.
Nice............. X(
but only 1 out of 10 for the method of extending the cable with an external joint half way up the garden by the fence....!
:shakehead
You can't see on the photo but all of the cores were nicked, probably with a knife, with the insulation cracked leaving visible copper conductor below.
My tests had shown a low IR and no continuity of the sheath..
following questioning, the customer then remembered a box about two thirds up the cable run.
Nice............. X(