I has a long argument once with the head of electrical engineering of my local council who was maoning that we had not bonded a door of an enlcosure that contained all type II equipment and armoured cable.The door should not require an earth. For street furniture removal of a door should not allow access to live parts and single insulated conductors, there must be internal barriers so the OPs is not compliant. Would I earth the enclosure, yes.
This isn’t @Fleeting going against the regs is it???The door should not require an earth. For street furniture removal of a door should not allow access to live parts and single insulated conductors, there must be internal barriers so the OPs is not compliant. Would I earth the enclosure, yes.
Thanks for the reply. Forgive my ignorance but could you explain why it’s non compliant.The door should not require an earth. For street furniture removal of a door should not allow access to live parts and single insulated conductors, there must be internal barriers so the OPs is not compliant. Would I earth the enclosure, yes.
The door cannot be used as a primary barrier there must be basic protection behind it. Removing the door on yours allows access to basic insulation this is not permitted there must be another barrier. See Regulation 714.411.2.201.Thanks for the reply. Forgive my ignorance but could you explain why it’s non compliant.
No you are misunderstanding. The door is not a layer of protection you must imagine it doesn't exist @Sidewinder is confusing with misinformation. When it comes to street furniture the access door is irrelevant when it comes to protection it is merely a means of access. Behind this access door there must be further barriers to prevent access to live parts and basic insulation.trouble is there appears to be a flex cable that does not have two layers of insulation . hence the lid needs to be secured in such a way that a tool is needed to open.
I am not confusing with misinformation.No you are misunderstanding. The door is not a layer of protection you must imagine it doesn't exist @Sidewinder is confusing with misinformation. When it comes to street furniture the access door is irrelevant when it comes to protection it is merely a means of access. Behind this access door there must be further barriers to prevent access to live parts and basic insulation.
Which clause?I am not confusing with misinformation.
Read the clause in BS7671.
Which clause in BS7671 would you be measuring this against?Expect this to be classed as C2 – POTENTIALLY DANGEROUS if the basic insulation is unsheathed anywhere where it may be accessible to touch. the picture showing the cable quite clearly missing a sheath
This fault may attract a C3 – IMPROVEMENT RECOMMENDED code if the cable is in an area not accessible to touch.
Regardless of whether accessible to touch or not, unsheathed basic insulation should not be in contact with metallic enclosure/sharp edges, this would be a C2 – POTENTIALLY DANGEROUS issue
So it does fall foul of the BS7671
You could say that about every metal consumer unit and 3 phase board.Expect this to be classed as C2 – POTENTIALLY DANGEROUS if the basic insulation is unsheathed anywhere where it may be accessible to touch. the picture showing the cable quite clearly missing a sheath
Soo by your reckoning you can have cables without the sheath out without protection. Section 714 doesnt agree or disagree...Which clause in BS7671 would you be measuring this against?
Section 714 disagrees with you.