been to look at a board change today, it's an old board with rewireable fuses, tn-s system.
There is a clamp around the sheath of the supply cable with a 4mm earth cable running up to the earth block in the current board, i assume this cable needs upgrading (tails are 16mm, so i assume the earth needs to be 16mm too even though Ze is 0.11)
Also there is no sign of bonding at all!! I did a continuity test from the gas pipe to the closest earth point (an adjacent socket) just out of interest and got a reading of around 60 ohms (i assume that confirms no bonding and the figure i'm getting is the path through the ground)
what do you think? does it sound as though the bonding is not there? it certainly wasn't visible from todays quick poke around.
I've been asked to put in a price for a new board and have mentioned the bonding to them what would you quote for new board and installation of bonding to gas and water?
I've done a few board changes before, but not domestic, and have all been pme and relatively straightforward
There is a clamp around the sheath of the supply cable with a 4mm earth cable running up to the earth block in the current board, i assume this cable needs upgrading (tails are 16mm, so i assume the earth needs to be 16mm too even though Ze is 0.11)
Also there is no sign of bonding at all!! I did a continuity test from the gas pipe to the closest earth point (an adjacent socket) just out of interest and got a reading of around 60 ohms (i assume that confirms no bonding and the figure i'm getting is the path through the ground)
what do you think? does it sound as though the bonding is not there? it certainly wasn't visible from todays quick poke around.
I've been asked to put in a price for a new board and have mentioned the bonding to them what would you quote for new board and installation of bonding to gas and water?
I've done a few board changes before, but not domestic, and have all been pme and relatively straightforward