been to look at a board change today, it's an old board with rewireable fuses, tn-s system.

There is a clamp around the sheath of the supply cable with a 4mm earth cable running up to the earth block in the current board, i assume this cable needs upgrading (tails are 16mm, so i assume the earth needs to be 16mm too even though Ze is 0.11)

Also there is no sign of bonding at all!! I did a continuity test from the gas pipe to the closest earth point (an adjacent socket) just out of interest and got a reading of around 60 ohms (i assume that confirms no bonding and the figure i'm getting is the path through the ground)

what do you think? does it sound as though the bonding is not there? it certainly wasn't visible from todays quick poke around.

I've been asked to put in a price for a new board and have mentioned the bonding to them what would you quote for new board and installation of bonding to gas and water?

I've done a few board changes before, but not domestic, and have all been pme and relatively straightforward

 
you will need DNO to upgrade that bit of 4mm, but since Ze is OK, they will just leave it or give you a nice large bill for it.

best option would be to put a earth block next to head, take 4mm to that, then your shiny new 16 from there to DB.

Gas and water earth will have to be done aswell

 
you will need DNO to upgrade that bit of 4mm, but since Ze is OK, they will just leave it or give you a nice large bill for it.best option would be to put a earth block next to head, take 4mm to that, then your shiny new 16 from there to DB.

Gas and water earth will have to be done aswell
Spot on reply old bean. Guiness Drink

 
Hi guys,

Yes new to your site,

round here we come across a lot of new cut outs at 80/100 amp but still with 4mm earth.

just a warning that was all.

didnt mean to cause confusion

regards

Fastham

 
Hi guys,Yes new to your site,

round here we come across a lot of new cut outs at 80/100 amp but still with 4mm earth.

just a warning that was all.

didnt mean to cause confusion

regards

Fastham
Welcome to the forum Fastham, I don't think you caused any confusion, Apache and Batty are very able to confuse themselves I believe.

Doc H.

 
Table 4.1 OSG 16mm tails require 16mm earthing conductor Bonding conductor can be 10mm CJS
Thanks for pointing that out. I cant remember the last time i did not use 25mm tails & 16mm main earth, so had forgot this changed in the 17th edition.

Can someone point me to a recent thread where a poster claimed if all circuits are RCD protected only a very small main earth is needed.

 
Thanks for pointing that out. I cant remember the last time i did not use 25mm tails & 16mm main earth, so had forgot this changed in the 17th edition.Can someone point me to a recent thread where a poster claimed if all circuits are RCD protected only a very small main earth is needed.
cant remember the thread..

but it was n. tessla as far as I remember? :)

 
THE HILLS ARE ALIVE.............................

WITH THE SOUND OF MUSIC!!!!!!

Guiness Drink:Y

Guiness Drink:Y

Guiness Drink:Y

Guiness Drink:Y

Guiness Drink:Y

Guiness Drink:Y

Guiness Drink:Y

Guiness Drink:Y

more communion wine vicar???

BlushingBlushingBlushingBlushing:p:^O:^O:^O

 
Top