Hi All,
Started some work on a garage conversion today (attached) moving some lights/sockets etc.
Ze to current earthing conductor 66ohms.
Must be TT (not sure where the rod is though) but the meter and head were changed in 2006 and it looks like its been given a PME connection because theres an earth block on the service head with nothing connected to it. Couldn't do a Ze because i couldn't get into the cu because the customer didn't want me to turn off the supply, but there was 230 between it and live.
My question is, if i do a Ze test to the terminal and get
0.35ohms can i just connect to it or do I have to get DNO permission?
AND
If i change the earthing do i have to do an EIC for the whole installation as i would with a CU change. Its a large house with a swimming pool and all sorts and that would be a hell of a lot of work for the piece of 16mm connecting the MET to the head?
Many thanks
Started some work on a garage conversion today (attached) moving some lights/sockets etc.
Ze to current earthing conductor 66ohms.
Must be TT (not sure where the rod is though) but the meter and head were changed in 2006 and it looks like its been given a PME connection because theres an earth block on the service head with nothing connected to it. Couldn't do a Ze because i couldn't get into the cu because the customer didn't want me to turn off the supply, but there was 230 between it and live.