Right,
Can't decide about this one.
Completed a PIR today on a "Portacabin" type building.
Located in a domestic garden.
Conctete base, water supply, fixed phone line installed.
Has been in place for 5 years and will hopefully be there for a long time to come yet.
Will need a road closure and a crane to lift it over the 2 storey house to get it out!
Brief desription of system.
Supply TN-S.
Hed>25mm tails>Henleys>25mm tails>KMF(40A) (& House board, in 25mm but this does not concern us)>25mm tails>NON DNO meter>25mm tails>Polymer enclosure with 40A 30mA instantaneous RCD>Polymer adaptable box>16mm SWA 3 core>DB in "Portacabin).
SWA is part buried part surface clipped.
Main earth 16mm.
Main bonding in house 10mm.
Water in "Portacabin" bonded to local DB in 16mm.
3 cores are LN&E.
Armour earthed both ends in 16mm to MET at one end & local board DB at "Portacabin".
Incoming water in copper.
Now I KNOW that the local DNO network in the area is PME.
HOWEVER the presntation to me is TN-S.
I have not checked the Z's at the origin I was only there to check the cabin out, perhaps I should have but after fitting the EM light & finding it was duff, that p*55*d me off a bit & I lost the plot!
Did all the tests on the cabin, all OK, Z's well low.
Could not isolate the house to do a Ze and this would have been very awkward and time consuming due to the layout.
Could NOT disconnect the DNO end of the earths as they were on a 951 clamp onto the sheath & the DNO guys round here are banned from touching these! To disconnect the 951 is a cable cut outside the property, remove the clamp install new means of earthing and reconnect mains!
Not overly bothered about the export, however, the "Portacabin" is a portable building, though not very in this case!
One thing is the make up of the building, inside all plasterboard walls, outside colour coated steel. This is very like a CARAVAN!
When I had my annual I discussed this with my AE as I had another PIR where by we had a PME supply and exported earths to external steel containers, however, these were within 2m of structural steelwork of the main building. There were other issues that had resulted in the containers being disconnected at the clients agreement. Hence why it was left like that. On the containers one, to split the earth system one would have conductive earthed parts touchable with 2 different earthing systems, so we decided that the local DB
Can't decide about this one.
Completed a PIR today on a "Portacabin" type building.
Located in a domestic garden.
Conctete base, water supply, fixed phone line installed.
Has been in place for 5 years and will hopefully be there for a long time to come yet.
Will need a road closure and a crane to lift it over the 2 storey house to get it out!
Brief desription of system.
Supply TN-S.
Hed>25mm tails>Henleys>25mm tails>KMF(40A) (& House board, in 25mm but this does not concern us)>25mm tails>NON DNO meter>25mm tails>Polymer enclosure with 40A 30mA instantaneous RCD>Polymer adaptable box>16mm SWA 3 core>DB in "Portacabin).
SWA is part buried part surface clipped.
Main earth 16mm.
Main bonding in house 10mm.
Water in "Portacabin" bonded to local DB in 16mm.
3 cores are LN&E.
Armour earthed both ends in 16mm to MET at one end & local board DB at "Portacabin".
Incoming water in copper.
Now I KNOW that the local DNO network in the area is PME.
HOWEVER the presntation to me is TN-S.
I have not checked the Z's at the origin I was only there to check the cabin out, perhaps I should have but after fitting the EM light & finding it was duff, that p*55*d me off a bit & I lost the plot!
Did all the tests on the cabin, all OK, Z's well low.
Could not isolate the house to do a Ze and this would have been very awkward and time consuming due to the layout.
Could NOT disconnect the DNO end of the earths as they were on a 951 clamp onto the sheath & the DNO guys round here are banned from touching these! To disconnect the 951 is a cable cut outside the property, remove the clamp install new means of earthing and reconnect mains!
Not overly bothered about the export, however, the "Portacabin" is a portable building, though not very in this case!
One thing is the make up of the building, inside all plasterboard walls, outside colour coated steel. This is very like a CARAVAN!
When I had my annual I discussed this with my AE as I had another PIR where by we had a PME supply and exported earths to external steel containers, however, these were within 2m of structural steelwork of the main building. There were other issues that had resulted in the containers being disconnected at the clients agreement. Hence why it was left like that. On the containers one, to split the earth system one would have conductive earthed parts touchable with 2 different earthing systems, so we decided that the local DB