We had the kitchen ring with high trip time for the RCBO the rest of the place was fine .
Trip time was 300mS , plus the tester dithered slightly , the two LED lights flicker, go dim then it trips.
Tried a second RCD tester ( Yes we are two tester firm) That flashed up reading of 7 which immediately faded , followed by "ERROR 5 " :C
Thinking its a faulty RCBO I swap with the next breaker but the same occurs, so wiring fault .
Readings were R1 = .22 / Rn = .38 / R2 = .43 / R1 + R2 = .69 Zs .3
We started checking ( not being paid for that) but there was a socket behind a built in fridge , for the fridge, old dear wouldn't let us remove the fridge ....." I should get the kitchen fitters back they will know how to remove it ." ( Two screws) Then didn't really want us to return to sort it so what do you do?
There,s something wrong somewhere but we've had to leave it .
The other trip times were :-
12
12
9
12
12
8
300
7.8
:C
Trip time was 300mS , plus the tester dithered slightly , the two LED lights flicker, go dim then it trips.
Tried a second RCD tester ( Yes we are two tester firm) That flashed up reading of 7 which immediately faded , followed by "ERROR 5 " :C
Thinking its a faulty RCBO I swap with the next breaker but the same occurs, so wiring fault .
Readings were R1 = .22 / Rn = .38 / R2 = .43 / R1 + R2 = .69 Zs .3
We started checking ( not being paid for that) but there was a socket behind a built in fridge , for the fridge, old dear wouldn't let us remove the fridge ....." I should get the kitchen fitters back they will know how to remove it ." ( Two screws) Then didn't really want us to return to sort it so what do you do?
There,s something wrong somewhere but we've had to leave it .