Hi
I have extension to supply. Extension is kitchen / diner downstairs. Bedroom / bathroom upsatirs.
Using oil combi for shower
Using gas for hob.
Rest of house wiring a muddle dont want to touch so want to run a new supply off exisitng wylex split rcd board to second small cu.
Length of cable from cu 1 to cu 2 is 32m
cliped direct
So calculations in extension are
ring - 32 amps
cooker (oven) 4.35 amps
lighting 5.22 amps - 12 lamps all together using the 100 watt rule but in theory they are led.
estimated demand 39.8 amps
distance 32m
use 3% for lighting
voltdrop 5.6 volts
max cable length 39.4 m
current capacity of cable 65 amps
therefore 10mm is fine.
10mm t and e from cu 1 to cu 2.
In cu 1 use a 40 amp rcbo as i cant get the cable more than 50mm from surface.
in cu 2 one 32 amp mcb for 1 ring sockets
one 6 amp mcb for 1 radial lights
oven will be fed from ring (1kw) via double pole fcu.
not ideal having lights and ring on same rcbo but if fault at least rest of house will have light - sockets. could split it into 2 rings for sockets and 2 radials for lights but seems overkill for 3 rooms?
I have extension to supply. Extension is kitchen / diner downstairs. Bedroom / bathroom upsatirs.
Using oil combi for shower
Using gas for hob.
Rest of house wiring a muddle dont want to touch so want to run a new supply off exisitng wylex split rcd board to second small cu.
Length of cable from cu 1 to cu 2 is 32m
cliped direct
So calculations in extension are
ring - 32 amps
cooker (oven) 4.35 amps
lighting 5.22 amps - 12 lamps all together using the 100 watt rule but in theory they are led.
estimated demand 39.8 amps
distance 32m
use 3% for lighting
voltdrop 5.6 volts
max cable length 39.4 m
current capacity of cable 65 amps
therefore 10mm is fine.
10mm t and e from cu 1 to cu 2.
In cu 1 use a 40 amp rcbo as i cant get the cable more than 50mm from surface.
in cu 2 one 32 amp mcb for 1 ring sockets
one 6 amp mcb for 1 radial lights
oven will be fed from ring (1kw) via double pole fcu.
not ideal having lights and ring on same rcbo but if fault at least rest of house will have light - sockets. could split it into 2 rings for sockets and 2 radials for lights but seems overkill for 3 rooms?