Is a 20mm black PVC rear entry terminal fitting a figment of my imagination ? Looked a few web site and none have them listed .

 
Sorry to ask again , PVC conduit supports page 115 of OSG table 4C horizontal spacing am I right in saying the saddles should be 400mm apart or is PVC conduit classed as rigid insulating with a horizontal spacing of 1500mm ?

400mm seems awfully close once its marked on the wall.

Cheers

Andy

 
I would say 400mm is correct but await being corrected. If you put the spacings further apart, over time the conduit looks like its bowed as looks sh*te as ive learned from when I put mine up about 8 years ago ffs.

Cheers

 
So its a work in progress still need another through and another 10 saddles and then the cable.

DSCF0537.jpg


DSCF0538.jpg


DSCF0539.jpg


DSCF0540.jpg


 
Well done Atty, looking good so far, nice bit of conduit bending there, did you use a spring?

 
Atty ????????????????

Yes i did only done a very small amout at college so far, so that was my first REAL trial of putting into practice what i have learnt .

 
Sorry Androiduk

Jumping around on so many threads got a bit mixed up there:Blushing

 
No problem Tim I got the idea many thanks. Managed to get the spring from my local B&Q under a fiver.

 