Have just moved into a house. Old re wire-able fuse box has been replaced. One of the circuits keep tripping the RCD.
Basically the circuit (3 lights) is fed off the boiler switch. The boiler works fine, only the 3 lights fed from the boiler switch are causing the RCD to trip.
There is continuity between all of the light switches, 240v between L&N though only 160v between L&E.
There is however only continuity between lives from the light switches and live at the boiler switch. No continuity between neutral and earth at any lights and the boiler switch.
Assuming the fault must be the wiring between the boiler switch and first light switch on circuit but can’t see any loose terminals. Any ideas ?