Evening all,
Been to look at a fault today! Customer said a socket was not working. Plugged my tester in and instead of reading saying 230v on phase and 230 on earth I got a 230 on phase, 187 on Earth and 33 on neutral. I took socket face off to check it was not a faulty socket(which it was not). Only one cable in back box and could see that it went under floor . All other sockets on circuit work and readings are fine. The circuit is 32 amp 60898 and split load board. All sockets on circuit only have one cable so must be jbsunder floor. Informed customer I would be back in morning to investigate properly.
Has any one had any experience of this type of problem before. Just wanted a few pointers before breaking circuit down ?
Been to look at a fault today! Customer said a socket was not working. Plugged my tester in and instead of reading saying 230v on phase and 230 on earth I got a 230 on phase, 187 on Earth and 33 on neutral. I took socket face off to check it was not a faulty socket(which it was not). Only one cable in back box and could see that it went under floor . All other sockets on circuit work and readings are fine. The circuit is 32 amp 60898 and split load board. All sockets on circuit only have one cable so must be jbsunder floor. Informed customer I would be back in morning to investigate properly.