Called out to a property last night by my sister, her neighbour came round in a panic(2 story extension & electrical work 9 months old)..."lights tripped I reset the mcb but now the consumer unit is sparking & when I turned the bathroom lights back on the mcb tripped again"
I got them to isolate the cu & made my way there;
Well the rcd sparking was a red herring, it was nothing to do with the lights, just a loose termination........
The bathroom lighting on the otherhand, if ever there is an advert for why you should not cover cabling (in this case it is 1mm T/E) & reccessed fittings under insulation in a loft space here it is:
http://i83.photobucket.com/albums/j293/gazjothomas/20120817_204446.jpg
http://i83.photobucket.com/albums/j293/gazjothomas/20120817_204458.jpg
http://i83.photobucket.com/albums/j293/gazjothomas/20120817_204504.jpg
3 of the four fittings were as above & the fourth was showing signs of browning on sheath.
They were lucky they had a reasonably upto date cu & not the old original 3036 boards that are in these properties. I say reasonably upto date as it is a 16th ed split load board.
Anyway outcome is they were not happy with the builders sparks originaly (had some problems with the sockets & things) so have asked me to undertake a EICR & fit new lighting in the bathroom (partial re-wire due to burning of cable)...
I got them to isolate the cu & made my way there;
Well the rcd sparking was a red herring, it was nothing to do with the lights, just a loose termination........
The bathroom lighting on the otherhand, if ever there is an advert for why you should not cover cabling (in this case it is 1mm T/E) & reccessed fittings under insulation in a loft space here it is:
http://i83.photobucket.com/albums/j293/gazjothomas/20120817_204446.jpg
http://i83.photobucket.com/albums/j293/gazjothomas/20120817_204458.jpg
http://i83.photobucket.com/albums/j293/gazjothomas/20120817_204504.jpg
3 of the four fittings were as above & the fourth was showing signs of browning on sheath.
They were lucky they had a reasonably upto date cu & not the old original 3036 boards that are in these properties. I say reasonably upto date as it is a 16th ed split load board.
Anyway outcome is they were not happy with the builders sparks originaly (had some problems with the sockets & things) so have asked me to undertake a EICR & fit new lighting in the bathroom (partial re-wire due to burning of cable)...