I think I have settled on a Solis 8kW hybrid inverter, S6-EH1P8K-L-PLUS ( SOLIS/12789/V1/A1 ) as the ideal solution for my array/battery setup. It is fully G99/G100 type tested.
I'm not that fussed about export and probably won't sign up for SEG payments so export is a low priority, but I wouldn't say no to free money I guess. Is it a question of chucking a G99 form in with the full 8kW output and seeing what they come back with? Is there a charge for just chucking in a speculative G99?
I understand they sometimes come back with a charge for network upgrade for G99 applications, can you reduce/eliminate that by implementing a G100 ELS with a lower value or even zero export value? I know from the grid capacity database that my local substation is showing plenty of headroom for reverse power capability, but the upstream isn't so not quite sure how that will pan out. There is some mention of witness testing, possibly for G99 applications over 32A ... but possibly not for fully type tested equipment. At the best part foa a grand, that is something I'd rather avoid.
The alternative would simply be to use an AC charger / off-grid setup where the connected device is not capable of generation and just avoid the entire G99 thing, but the particualr inverter above would be a neat single-box solution ...
I'm not that fussed about export and probably won't sign up for SEG payments so export is a low priority, but I wouldn't say no to free money I guess. Is it a question of chucking a G99 form in with the full 8kW output and seeing what they come back with? Is there a charge for just chucking in a speculative G99?
I understand they sometimes come back with a charge for network upgrade for G99 applications, can you reduce/eliminate that by implementing a G100 ELS with a lower value or even zero export value? I know from the grid capacity database that my local substation is showing plenty of headroom for reverse power capability, but the upstream isn't so not quite sure how that will pan out. There is some mention of witness testing, possibly for G99 applications over 32A ... but possibly not for fully type tested equipment. At the best part foa a grand, that is something I'd rather avoid.
The alternative would simply be to use an AC charger / off-grid setup where the connected device is not capable of generation and just avoid the entire G99 thing, but the particualr inverter above would be a neat single-box solution ...