you could make the installation TT, but you would then need 2 rods min, one at star, and one at installation (and you would have to ditch earth connection between the 2). but if the genny gives TNS, why bother with TT? just creates extra work, and extra risk, for no reason.so why does the genny require a rod then?why do the DNO rod star point on a TNS distribution?
to make the install a TT is explained in my post,
the whole reason it has a rod is so there is a return path to star, so if someone was to touch a live conductor, it can flow through earth, back to star, and trip any RCD. no rod at star means under fault conditions (to ground/soil) will mean a voltage between genny frame/earth, to ground.
unless you omit the earth between genny & installation, and use a rod at each end, the supply will be TNS
i would draw you a diagram to illustrate this, but since TNS is well known, there is already a diagram in 7671 (fig 2.3, page 33, and then fig 2.5, page 34)
you welder theory, whilst i agree with the results of the welder not working with a small genny, has absolutely nothing to do with earthing arrangements