so why is this test done?
Generally Zs testing of circuits is to ensure correct disconnection of times of CPD's are met,
when comparing with the max Zs tables, corrected by 0.8 (rule of thumb)
is the Zs at DB test at board 1 done to compare the Zs reading as mentioned previously,
to ensure the main fuse in the service head complies with the disconnection times?
Go back to your opening question.....
"
Generic Schedule Of Test Results, Completion"
The form is a generic form that is designed to allow its use on single or multiple board installtions...
As you say the Zs readings we take are to verify max disconnection times in relation to final or distribution circuits that we have designed and installed and selected cable sizes and protective devices..
The incoming earth loop impedance at a board is IMHO informative, to identify that you do have an adequate earth coming into that distribution board..
On a single installation board the earth loop impedance component that is outside of our installation is called the Ze...
If its a multiple installation board then its called Zs at board or Zdb...
Whatever you call it the compliance with disconnection time bit is only relevant when you have a final or distribution circuit with its cable size and protective device details...
This data would be on the schedule for the suppling board not the board that the sub-main feeds
Whereas if it is a single board installation it is just a reading to verify the integrity of the incoming earth...
As you have NO design or installation powers over the suppliers fuse...
That is their property.. their jurisdiction..
And BS7671 does not cover the distribution element coming into your property (exclusions 110.2 (i))
What faults are you expecting at incoming supply to a single board... Dead short L-N or L-E...?
So disconnection times of the service fuse is IMHO of far less important than the short circuit capacity of the switch gear in relation to your prospective fault which you write on the line below!
From reading your posts I think you do know what Ze & Zs are and their purpose..
But you are just getting unnecessarily concerned about a box on a form that in the case of a single CU is pretty much irrelevant as the information is on page 1 of the generic test certificate anyway!!
Its just a matter of common sense thinking what is this reading, why am I doing it, and which boxes on which forms are relevant to my installation... (as some are not relevant in every case!)
Just looking back at the sample form on page 159 OSG that you mention..
In that illustration two lines down you have "Correct Supply Polarity Confirmed" they write N/A...????
Why would you not verify polarity incoming to your Consumer unit???
As another side note...
I use the NIC forms..
Their schedule of test results does NOT have the Ze / Zdb / Zs @ board ...
Just the Fault Current at board!
Take the OSG sample form as an illustrative example...
NOT a set-in-stone rule you must follow!
opcorn