Testing hasnt been done yet. So far, a lot of time has been spent doing a very thorough visual! If necessary, FI will be done.IMHO you are worrying about the wrong problem....
Unless this is a really really big property..
which I am guessing it isn't, (as only 4-way wylex box)..
I would be very worried if max Zs for some 60898's cannot be met on a domestic TN-s system?
e.g. a 6A 60898, type B Max Zs 7.28.. (table 41.3 pg 62)
so lets minus off 0.8 worth of possible Ze for a TN-S..
that gives us 6.48ohms worth of R1+R2 portion of the Max Zs.. (R1+R2=Zs-Ze)
So 6.48ohms is around 179m of 1.0mm/1.0mm T&E,
Or 214m of 1.5mm/1.0mm T&E...
{on a lighting circuit}...
150+ Meters is a BIG domestic lighting circuit!!!
How BIG is this house??
(Do the sums for 16A / 32A 2.5mm & 6.0mm)...?
If you cant get your Zs on a domestic TN-s, then as Murdoch say's, it needs FI..
Not a cowboy get out of jail 30ma RCD card!!!!
P.S.
How are you meeting 314.1 (i) with just a single 30ma upfront RCD?
:C
Agreed..
No need for tin hat IMHO!
Guinness
Did a cowboy write 411.4.204? And did cowboys teach and write the literature for the 2391 course??
(Using an RCBO on a TN-S if really necessary wasnt my idea to cut corners!)
If prolonged FI, should for example, point to the fault being located buried somewhere that would involve ripping the place to pieces to get to it, and the Zs is just a bit out, then I suppose this would be an example of a circumstance why you may opt to use of an RCBO??
314.1 (i) wont be met (it never has been in this property) because the house was wired with up&down lights into one way, and up&down sockets into one way. It has been like that since late 60's/early 70's!