I am wiring 3 x 1650 w hand dryers is a 4mm radial circuit on a 32 amp breaker suitable ? Thanks

 
Hello matt77,

Welcome to the forum.

What have you got from your circuit design calculations, post them up and we'll look over them to see if you have made any errors or overlooked anything.

 
Yes 

But we all have different ideas ,  I'd have probably gone 2.5.mm radial   on a 20A  as they are only on for 1 minute each time .  But thats me , 4mm seems a bit OTT .    13A Spur at each one , if they all operate together it won't be for long.    Not knowing the cable run etc . 

We'll now get a thousand versions , which should be interesting . ;)

 
Last edited by a moderator:
The cable run is 50 to 75m though loft insulation ,in a busy training centre and the will be in use a lot

 