tom1
Distinguished Member
- Joined
- Aug 7, 2009
- Messages
- 2,330
- Reaction score
- 0
1. cooker circuit.
32 amp mcb, 6mm cable to cooker switch then 6mm to connection plate to feed 45 amp hob. that bits fine, then i took a feed from the connection plate in 2.5mm to feed a 20 amp oven. i think its ok but i could do with a second opinion thanks.
2. 10.6 kw shower put this on a 50amp mcb, a more experianced spark told me to put it on a 40 amp as it would not draw enough power for a 50 amp.
now i need to issue and iec, should i change it back. osg says the mcb can only be higher than the rated current of the appliance never lower.
3. put the imersion on its own 20 amp mcb as it was running off the light circuit 10 amp, also put a towel rad on it. is this a case of a note on the cert under deviations.
thanks for the help
32 amp mcb, 6mm cable to cooker switch then 6mm to connection plate to feed 45 amp hob. that bits fine, then i took a feed from the connection plate in 2.5mm to feed a 20 amp oven. i think its ok but i could do with a second opinion thanks.
2. 10.6 kw shower put this on a 50amp mcb, a more experianced spark told me to put it on a 40 amp as it would not draw enough power for a 50 amp.
now i need to issue and iec, should i change it back. osg says the mcb can only be higher than the rated current of the appliance never lower.
3. put the imersion on its own 20 amp mcb as it was running off the light circuit 10 amp, also put a towel rad on it. is this a case of a note on the cert under deviations.
thanks for the help