Hi fellas.

Hoping for a little help.... wiring in 2 separate uh3 wiring centres for 2 separate heating manifolds... plumber is using heatmiser system. Question is do i need to run separate circuits for each wiring centre or just run a radial circuit to incorporate both. Hope this makes sense.

Cheers

 
We completed an installation recently and had a radial circuit feeding a switched fused connection unit which supplied all heating/hot water controls, which included 3 X UH3.

 
Cheers for you reply Steve... the only reason for asking really was because the plumbers are locating the 2 uh3 at either side of the house.

 
It would be normal to have all heating controls on one circuit. you wouldn't feed the manifold from one circuit and the boiler from another would you?

 
Cheers Dave... that was kinda my thoughts on it but it is nice to have confirmation when installimg something new for the first time.

 