This string started me thinking about how the earthing of a big welder would be arranged.
This led to recollection of an incident a few years ago, when a friend of mine, a professional metal-worker, momentarily put down his welding rod on an adjacent guillotine machine, and immediately burned out all its wiring back to the distribution board.
I can tell you all about this, being a properly qualified welder...
It is exactly as sidewinder has written.. The problem was with old welding sets..
For some reason, some idiot that wrote the british standard for welding sets decided that the secondary winding be earthed to the case of the set. Why this was, is beyond me at this time of night!!
Anyway, what would happen is this; You have two leads for welding, yes?? The lead to the rod holder, and the return lead [that is the proper name for it, NOT an "earth" lead] it is the WELDING RETURN LEAD.
Now, for safety reasons, you DID have a "welding earth". This was a lead that went from a good earth, say like the frame of the factory, to the "job", the thing you were welding. This was to stop the job going up to welding voltage, [relative to the ground it was stood on etc] which was usually 80-100V in them days and also for safety in case say the lead of a drill etc got squashed.
What the problem would be is this.. Picture this.. The secondary windings are earthed to the frame of the welder.. The welder is then earthed back to the MET. The job you are welding is ALSO earthed to the frame of the building, which is also bonded to the MET.
Mr welder forgets to connect the welding return lead, sticks in his 6 SWG iron powder rod and off he goes at 400A...
Ooer.. The current path now [with the return lead missing] is from one end of the secondary winding, down the welding cable, down the rod, across the arc gap, through the workpiece, down the "welding earth" to the frame of the shed, through the bonding cable that runs from the shed frame to the MET in the DB, back down the circuit wiring CPC to the welder socket/isolator whatever, down the welders supply lead, back to the case of the welder , which some dumbo decreed be connected to the other end of the secondary..
Result?? You burn out the entire earthing arrangement for that entire circuit back to the board, AND possibly many other circuits too, AND the bonding arrangements for the entire factory...
Apparently, the use of "welding earth leads" is now discouraged.. Something to do with TNCS perhaps????
Anyway, if a welder trips an RCD there is something wrong with it, so do not worry about that, AND, if you DO come across an old welder where the secondary is bonded to the case, the thing should not be used...
john..