Help with College task
Mike Irving
Jul 31, 2016
7
Hi guys, I'm a 3rd year electrician student and need some help.
I've been giving a task to do over the summer, it involves selecting a wiring system for a lighting circuit in a Army barracks switch room...The Fluorescent Luminaire
are 1800mm 2*70w ip65 and the cable is going to be in Galvanised conduit.
the building has 51 fluorescent tubes split into 4 room, which will be on 4 individual circuits
Sub station 16 tubes
Switch room 25 tubes
Work shop 12 and Maintenance room has 6
When working out the switch room for example the calculations i am using are (2*70*25)/230v gives me 16.52A so the breaker i would use is 20A is this right.
Kind regards
Mike
The question states that the circuits are to be split over 4 lighting circuits. Bear in mind that most lighting accessories are only rated at 16amp max.
You need to do a break down of all circuits and wire them accordingly. Remember switching.
It doesn't say...the only info I have is the electricity supply is 11kV/400/230V.....I assume it would be single phase.....
Oops it should be 8 in the sub station 25 in the electrical switch room 12 in the workshop and 6 in the rest area...
I get 15.21A, so a 16A breaker would do. Probably a Type C. Use banks of switches, eg 1 switch for 5 luminaires. Metal Switches (army fingers). Possibly separate cpc single in conduit for high earth leakage current from all those ballasts?
Cheers.....
Or you could use a contactor to switch the load. But switching in banks as Rob said would be the best option.
Do you have to do the cable sizing as well?