Help with Electrical design unit Level 3
Sparkywannabe
Mar 18, 2020
I've done most of the stuff but something doesn't add up to me at the adiabatic equation.
Question 5
Regulation 543.1.3 of BS7671 for Fridge circuit 2
Wired in 70°C single core t/p in pvc conduit
Ambient temperature 35°C
protective device BSEN60898 16A Type C
Length of run is 9.15m
Quoted fault at pool/cafe 3.7ka
R1+R2 = 14.82x1.06x1.2x9.15÷1000= 0.17Ω
Zdb value = 0.11Ω
 Zdb+ (r1+r2) = 0.11+0.17= 0.28Ω
Zs= 0.28
Ipf = Vo÷0.28 —> 230÷0.28=822A
Adiabatic equation
S=√I2T÷K
S=√8222x0.1÷115= 2.26mm2
The cross-sectional area for the fridge circuit 2 is 2.26mm2 which complies with the regulation 543.1.3 of BS7671.
Hi I am also trainee like you but There are something that I dont understand in your calculations .
you stated R1+R2 = 14.82x1.06x1.2x9.15÷1000= 0.17Ω   could you explain where did you get 1.06 from??? as this circuit is  70  degree so I am assuming its incorportated so I3 would be 1.20  or if not incorportated than it would be 1.04??
Furthermore I found max R1+R2 = Zs max-Ze/ I3*Length multiply 1000  which gave us 115.17 so I went to I1 table Onsite guide and choose 2.5/1  which is 25.51
using this in  Zs=Ze+(R1+R2*Length*1.2/1000) gives us      0.11+0.28  =0.39
IpF=  230/0.39     =  589.7
Adiabetic equation
S=√I2T÷K
S=√589.7^2*0.1/115
=1.62 mm
so the next available you can choose is 2.5 CPC