What strikes me from the graph is that you appear to be generating from PV very early in the morning to quite late into the evening but at the same time load consumption follows the increase / decrease in PV input. Bit suspicious that.
Can't believe you're adjusting your consumption to match the PV output that well.
There's also suspiciously next to no load consumption when the PV has gone to sleep. (unless you run around and turn everything off when the sun goes in

)
Do you have a feel for what your "normal" daily consumption is / was before the installation?
What size is your installation?
inverter / battery / PV array(s).
What's the PV array orientation? East / West /South _ Split?
Is that battery discharge from 100% or is it just hovering around the 10-15% level?
What is the system priority set to? Grid First, Battery First or Load First.
How is the system measuring import / export?
Is it metered or CT clamp?
If CT clamp where is this positioned?