Riggy
Senior Member
Did anyone actually answer the OP's question?
plumber,My redYou also need to look at arcing and pre-arcing times as well as I^2t, energy let through,
Sidewinder, For backup protection why would i need to consider the pre arcing, were not talking about discrimination?
and the fault limiting of the incoming supply.
as i said the total let through of the 1361 would need to be compared to the rating of the mcb(icu)
Also the downstream protective device does not need to be re-useable after a fault,
I stated the icu of the mcb This is the maximum it can break safely although it may no longer function
Steptoe
if we have a fault of 5000A then the mcb is effectively going to weld itself closed,
but the BS1361 will blow, fault >80A, but <33000A .
if the main fuse blows then we are going to change all secondary protective devices as a matter of course,
would that make sense?
Many fuses and mcbs offer energy limiting properties, especially on high fault currents, the fuses will break of the first half of the fault cycle. Take for example a 1361 type ii busman lr85 if we have a pfc of 33ka the fuse limits the let through to just over 10ka so if the downstream fuses were rated to say 15ka then backup protection has been afforded.
regards chris
what happens is the fuse ionises(Im sure thats not the right term but no one has said so yet)Thought you might find this useful http://www.talk.electricianforum.co.uk/showthread.php?t=590 If you had a re-wirable fuse fitted a fault current of >1kA can cause the fuse to go explosively. So if the upstream fuse can take a fault current of >16.5kA I would assume that the downstream re-wireable fuse would be blown to bits with a fault of 3 or 4kA.
The other question is how likely is this to happen? To cause this the fault must occur on one circuit pretty damn close to the fuse board to ensure there is a low enough R1 + R2 or R1 + Rn to allow such a large current to flow anyway. I'd be interested to know if anyone has ever seen the effect - and more particularly ever seen it in a domestic environment.
defo not got the mcbs wrong way round the 3871 are m6 the 60898 is a replacement for the 2871 and is only rated at 3kA.Andy,Sorry I don't think your post #2 did answer the OP.
Never mind, it has brought up a lot of discussion which is good!
Re-reading the OP mind I think he has god his 3871 & 60898's the wrong way around.
3871 typically M3 - 3kA, 60898's normally 6kA minimum unless we are talking about the plug in type to replace 3036's and I can't remember the ratings of these?
deffo the opposite from vaporiseAlbert:I think you wanted vaporise mate.
Ionising is somewhat different
thats itKME,What steps is describing is a chain ionisation reaction though, it is the formation of a plasma ball where by the air actually conducts, and the explosion can grow out o all proportion.
This is normally limited by the available current and the arc voltage though.
BTW, been away?
thank youi thought step had it right, type in 'jacobs ladder' on you tube i believe that to be ionization (yes sometimes i get very bored)
or PSCC of course.1, we make sure the downstream mcb has a rating greater than the pfc
regards chris