Think you should all look at the back of the regs in the appendix as the BS1361 standard is no longer as it has been withdrawn it,s a BS 88-3 now and has been since 2007 harmonisation again
Phone and argue yourselfI suggest the niceic guy is wrong, it wouldn't be the first time, you give him the let through value at 16ka of a 1361 type ii fuse which is 9 ka and ask him if a mcb rated icu 6ka is protected if he says yes then he shouldn't be on the help desk.
regards chris
Cheers Chris, I agree... but the point they made to me was that 22k was above the maximum stated by the DNO, and that we only need to work to the maximum PFC stated by them - which does fall safely within the limits of the suppliers fuse.But that's where the maximum pfc is 16.5ka, you had 22ka
Though at 22ka, a busman 1361 type ii 100 amp would only let through 8ka at that fault level so in my opinion no issues with a 60439-3 board but iwould expect mcbs with an icn/icu of (10000)