with a Ze that low on a TT I reckon they must have skimmed the neutral of the incomer with the rod!
either that, or they have hit the sewer ! :slap
either that, or they have hit the sewer ! :slap
Believe it or not I've actually done that! The place was earthed by the water pipe originally, around 70 ohms as I recall. I put in a new split load CU with 100mA type S main switch & 30mA on the split (16th Ed.) & banged a rod in by the back door step. 0.34 ohms...with a Ze that low on a TT I reckon they must have skimmed the neutral of the incomer with the rod! either that, or they have hit the sewer ! :slap
I'm learning a lot from these later posts, thanks guys....Ze should be measured just on the main earth conductor (disconnected from MET) to avoid any parallel paths caused by bonding etc. If you measured directly from the MET without disconnecting the main earth conductor (whatever the earthing system) you will probably get a lower reading due to a parallel path. In the scenario I outlined in post 100 we measured below 0.5 ohms at the MET with the main earth conductor and main bonding disconnected, the lowest resistance parallel path was through the immersion flex to the immersion, the tank & the old cast water pipes under ground.If the guys testing Daba's house just did a simple eath loop impedance test at the MET with main earth conductor, bonding conductors and final circuit CPCs connected the value they measured includes all the parallel paths and is not Ze.
What do you mean??? You still haven't proved that your installation (or appliances) are not the cause of your problems.I'm learning a lot from these later posts, thanks guys.... e.g.
1. Ze has been measured (twice) with all the "parallel paths" still connected and gives me no re-assurance of my own path to earth... BAD
2. IR tested globally across the board isn't a true test, probably devised by Haste because it is quicker (and therefore cheaper)... BAD
But, happy I haven't had to pay for these crappy cheap nasty tests... GOOD
We are waiting to see if the new RCD "immunises" me from the impulse the pub is generating - so far so good (8 days and counting).
Would you do that ?Don't know why he didn't just have the rcd, taken out in the first place???? :C
THEY (as in the DNO.) didn't supply the new trip - I had to get it, at my cost (they will reimburse me if it don't cure the problem).then again, I wouldnt have done a Ze on a TT install either,anyone else wondering if its a 30mA RCD they replaced it with?
i doubt this guy has a box small enough to contain his thoughts...so he has changed an old standard 200mS tripping RCD for a new EN one that is only required to trip in 300mS,well, you have to hand it to the guy for his thinking outside the box.
I hear you. It seems that the so-called "professionals" take short-cuts, and adopt bad pratices when doing their tests....OK,daba, I have been without good internet for a few days, reasons irrelevant, but here are my leanings so far if you wish to digest them.
1st thing, your 'Ze' on a TT is totally wrong, I do not think this is a true Ze at all, if it is a true Ze then I think this may well be a cause of a lot of your problems.
you need an Ra of your earth rod, your testers have not tested your earth at all if they have not measured your Ra, very reminiscent of people that have no idea how to test TT systems, or simply do not have the necessary equipment to do so, I would go for the former.
this is my first major concern, so until you actually have a proper earth resistance test done you are still at a lose, I take it you understand the difference between Ra and Ze as opposed to Zs and Zdb.?
in my humble opinion everything else that has taken place after this most basic of tests can be regarded as irrelevant until this one thing is proven.
Have just spoken with Haste technical about the apparent low N-E reading, and he confirmed that it is a typical figure obtained when testing with CB's closed, i.e. all the devices in the house connected, and is due to all manner of things, including, he said, the main culprits being surge suppression devices built into equipment. He confirmed that the "Limited Electrical Condition Report" is satisfactory in every detail, and I have nothing to worry about.
He said it was a test they devised themselves - I'm not going to argue with them.
Never heard of anything like it! Anyone else?
really?I hear you. It seems that the so-called "professionals" take short-cuts, and adopt bad pratices when doing their tests....1. The DNO tested my RCD with a device they plugged into a nearby outlet
2. Ze measurements were done with bonding connected
3. IR appears to have been done with all the breakers closed (sheesh 500V P-E and N-E applied to all the devices in the house!!)
Yet, my installation has stood up to all their mickey-mouse testing, and they still haven't investigated the CAUSE, not the EFFECT.
---------- Post Auto-Merged at 01:28 ---------- Previous post was made at 01:21 ----------
I meant to say "and they still haven't investigated the CAUSE, but investigated the EFFECT."
I have the evidence that another consumer is tripping my RCD - who is the governing body, the equivalent of Ofcom, or Oftel that I can make a written complaint to ?
Okay, so here's the evidence I have - it's about the best I can do...really?well, why havent you told us that then?
because none of the information you have posted here is anything like near the sort of factual information you will require when it goes to court, all you have so far is opinions and circumstantial evidence, no actual facts,
if you do indeed take your test results,[as reported to us], into court, then I think you may have a lot of people laughing at your evidence so far!