Todays problem from my letting agent:
Rented house, gas central heating.
Letting agent calls, says boiler has just been serviced, and the gas man says an electrician is needed to fix the timeswitch.
So I go and look. the time switch is not even connected.
It looks a fairly recent (but not brand new) Worcester combi boiler, so I'm guessing the timeswitch has not been connected since the boiler was changed, whenever that was, because the old wiring was incompatible.
The way it was wired was a 3 core and earth from the boiler (in the garage) to the timeswitch (in the utility room). Wired as live and neutral to the timeswitch, and switched live back to the boiler.
But the new boiler doesn't want switched live, it wants a volt free contact to switch a 24V circuit inside the boiler.
So my problem, how to re connect the timeswitch (which can be configured as a volt free contact) using just the existing 3 core and earth between the boiler and timeswitch. It's a major job to run another cable along this route.
My 2 "solutions" with their problems are:
Solution 1: the nasty dirty solution. Use 2 cores of the 3c&e for the L and N feed to the timeclock, and the third core plus the CPC as the low voltage switch contacts.
I don't like that as I don't like using a CPC for anything other than it's intended function, but there is in fact no need for a CPC at the timeswitch, and it would only be for a low voltage circuit.
Solution 2: Use just 2 cores of the 3 core and earth for the low voltage switch contacts. Then source a completely new L and N supply for the time switch from a FCU from a nearby ring main in the utility room.
Much better technically, but has the problem that the timeswitch is fed from a different supply to the boiler. Shouldn't be an issue but should I put a warning 2 feeds label on the timeswitch?
Anyone got any other suggestions?
Rented house, gas central heating.
Letting agent calls, says boiler has just been serviced, and the gas man says an electrician is needed to fix the timeswitch.
So I go and look. the time switch is not even connected.
It looks a fairly recent (but not brand new) Worcester combi boiler, so I'm guessing the timeswitch has not been connected since the boiler was changed, whenever that was, because the old wiring was incompatible.
The way it was wired was a 3 core and earth from the boiler (in the garage) to the timeswitch (in the utility room). Wired as live and neutral to the timeswitch, and switched live back to the boiler.
But the new boiler doesn't want switched live, it wants a volt free contact to switch a 24V circuit inside the boiler.
So my problem, how to re connect the timeswitch (which can be configured as a volt free contact) using just the existing 3 core and earth between the boiler and timeswitch. It's a major job to run another cable along this route.
My 2 "solutions" with their problems are:
Solution 1: the nasty dirty solution. Use 2 cores of the 3c&e for the L and N feed to the timeclock, and the third core plus the CPC as the low voltage switch contacts.
I don't like that as I don't like using a CPC for anything other than it's intended function, but there is in fact no need for a CPC at the timeswitch, and it would only be for a low voltage circuit.
Solution 2: Use just 2 cores of the 3 core and earth for the low voltage switch contacts. Then source a completely new L and N supply for the time switch from a FCU from a nearby ring main in the utility room.
Much better technically, but has the problem that the timeswitch is fed from a different supply to the boiler. Shouldn't be an issue but should I put a warning 2 feeds label on the timeswitch?
Anyone got any other suggestions?