spinlondon
Distinguished Member
- Joined
- Apr 18, 2009
- Messages
- 1,388
- Reaction score
- 0
Gonna have to ask you to explain?don't think so spinso 2.5mm singles L & N and 4mm earth
as long as VD is covered
Gonna have to ask you to explain?don't think so spinso 2.5mm singles L & N and 4mm earth
as long as VD is covered
i don't think that the 4mm rule for expected high leakage currents applys to single earth conductor only. i.e a ring will need 4mm earth alsoGonna have to ask you to explain?
How does that relate to using two 2.5mmi don't think that the 4mm rule for expected high leakage currents applys to single earth conductor only. i.e a ring will need 4mm earth also
How does that relate to using 2X 2.5mm
I'm not suggesting that the line conductors need to be 4MMnormally a ring would consist of 2.5 L&N and 1.5 earth but because of the high earth leakage we have to use 4mm earth but that does not mean the line conductors need to be 4mm too.so it doesn't matter if its a ring or radial it still needs 4mm earth
yes, for a single copper protective conductor (543.7.1.3(ii))do we not require minimum 4mm cpc if leakage exceeds more than 10mA total per circuit?
don't think so spinso 2.5mm singles L & N and 4mm earth
as long as VD is covered
Yes it is compliant.when I read 543.7.1.3(iii) it refers me to 543 In which there is a section on high earth leakage; 543.7 I
n which there is a reference to 543
headbangheadbangheadbang
I still think 2.5mm conductors and 4mm earth is compliant.
or maybe 2.5mm or 4mm T&E with extra 2.5 single cpc
:coat
PS How can we connect cpcs independently when CU has one earth block?
we had to add an earth bar to db's on a job once it was carp i tell theewhen I read 543.7.1.3(iii) it refers me to 543 In which there is a section on high earth leakage; 543.7 I
n which there is a reference to 543
headbangheadbangheadbang
I still think 2.5mm conductors and 4mm earth is compliant.
or maybe 2.5mm or 4mm T&E with extra 2.5 single cpc
:coat
PS How can we connect cpcs independently when CU has one earth block?
Yes it is compliant.If using two conductors as CPC, the two do not have to add up to 4mm
yes but the 543.7 is the section that deals with high earth leakage not 543.1The reference to section 543.543.7.1.3(iii) "Two individual protective conductors, each complying with the requirements of Section 543."
"543.1.1 The cross-sectional area of every protective conductor, other than a protective bonding conductor, shall be:
(i) calculated in accordance with Regulation 543.1.3." etc.
One of the anomolies of the Regs. I'm afraid. Probably be sorted next year with the amendment.yes but the 543.7 is the section that deals with high earth leakage not 543.1round and round we go! Wet Fish chicken or the egg????
bad day explode