I was doing an insulation resistance test today on a newly installed Lighting circuit, (1.5mm 6242y ,hall/landing, and a couple of outside lights) 5 downlights on the hall landing and stairs, and two outside lights, I've used wagoboxes for the interconnections, as the downlights have removable loop in/out plugs and sockets fitted on them. I tested the downlight chain first before connecting in the loop to the outside lights, all good, resistance of over 199 Mohms, however when I looped in the outside lights the reading fell to 150 Mohms.
Logic dictated that the lower value was the fault of the outside lights, but doing a test just on that loop also gave a reading of greater than 199 Mohms, I isolated all the cables in that circuit, tested them all individually, removed the 2 light fittings and tested them, all giving a reading of greater tan 199 Mohms.
Connecting either or both of the outside lights to the overall circuit reduced the insulation resistance to around 150 Mohms.
I realise that this is a high and quite acceptable value, and if, like many test instruments that read up to 99 Mohms had been used I would have been totally unaware of any reduction.
The results don't seem to make sense though, and the only solution that I can come up with, is that possibly the resistance value of each leg of the circuit is over 199 Mohms, too high for the meter to read, but when they're both connected together the combined value of the two legs , effectively in parallel is lower that the 199 Mohm limit of the meter?
Though, having said that, the entire outside light circuit from the junction box including switch drop is no longer and about 6 metres long, so there should be very little leakage resistance. I've used a CK automatic cable stripper, wondering if anyone's had any problems with the inner conductor insulation being damaged when removing the outer sheath with an auto stripper?
Any comments would be appreciated thanks!
Logic dictated that the lower value was the fault of the outside lights, but doing a test just on that loop also gave a reading of greater than 199 Mohms, I isolated all the cables in that circuit, tested them all individually, removed the 2 light fittings and tested them, all giving a reading of greater tan 199 Mohms.
Connecting either or both of the outside lights to the overall circuit reduced the insulation resistance to around 150 Mohms.
I realise that this is a high and quite acceptable value, and if, like many test instruments that read up to 99 Mohms had been used I would have been totally unaware of any reduction.
The results don't seem to make sense though, and the only solution that I can come up with, is that possibly the resistance value of each leg of the circuit is over 199 Mohms, too high for the meter to read, but when they're both connected together the combined value of the two legs , effectively in parallel is lower that the 199 Mohm limit of the meter?
Though, having said that, the entire outside light circuit from the junction box including switch drop is no longer and about 6 metres long, so there should be very little leakage resistance. I've used a CK automatic cable stripper, wondering if anyone's had any problems with the inner conductor insulation being damaged when removing the outer sheath with an auto stripper?
Any comments would be appreciated thanks!