- Joined
- Feb 27, 2008
- Messages
- 11,018
- Reaction score
- 0
Theres your problem never trust them wylex consumer units. Damn have two to fit tomorow.simple answerNo
Its a standard 5 + 5 wylex split load
Theres your problem never trust them wylex consumer units. Damn have two to fit tomorow.simple answerNo
Its a standard 5 + 5 wylex split load
Yes and everything checks out fine there no continuity onto other circuits.OK, Dane:Have you checked for continuity to another circuits CPC and or Neutral?
Don
OK, with the ring main connected to the CU, remove the other circuits one by one (connection by connection if you have to).Yes and everything checks out fine there no continuity onto other circuits.
40,000KohmsRemoved the ring main, tested it all fine. Once the ring is put into the board it fails tests insulation resistance to any earth is around 0.04M
No it doesn't need to be a very wet building for a reading of 0.4meg.Not usual at all. It threw myself and another completley at first. Was loosing light by 4.30 so had to pack up and got to go back in the morning.
Going to rip the ring main apart like you say lurch....
Some how, some where that 1 piece of cable is going to earth via the building. Again, there are no other metal parts within the builing.
Cables are all in plastic capping... yes it could be a capping nail! But its must be a very wet building on the structure side to get a reading through the building like this surely?
never had anything like it before though so its a very strange one to me.DON'T BE FOOLED THINKING MEGOHMS DON'T GO THROUGH BRICK!
:|
I think someone is. Even if it was a TT you would still get a Ze reading if you connected the earth to the neutral block on the incomer.I know its not what you should do, but we took the neutral cover off the main incomer and but a seperate earth in And the reading was the same, no earth .....
Am i missing something here? Wet Fish
Ive not actually been to the job today it some one who does a bit of work for meThere is a big sticker "this is a PME System - a minimum of 10mm tails are required"
well, that sounds like a give away as to what it is....There is a big sticker "this is a PME System - a minimum of 10mm tails are required"
you made it a long time! im good. obviously your doing so well you dont have time to come here often!ooohhhhhh andy ..... long time how the devil is you .