Intermediate to 2 way lights confusion : )

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

Electric_Yoda

Junior Member
Joined
Oct 21, 2008
Messages
15
Reaction score
0
Hi guys

Going to look at a friends lights tomorrow.

Basically he has a long hall/kitchen - light in hall, light in kitchen. Both lights operate together.

Switch at either end - one in hall, one in kitchen. Halfway along intermediate switch also.

He wants it so each light operates independently. And change the intermediate to a 2 gang 2 way to operate either. So basically making it into 2 x 2 way setups

Now ..... bear with me ...I always get confused when I think too hard about lights :_|

Am I right in thinking I will need to run another switch cable in ? Its not as simple as just changing the intermediate switch for a 2G 2Way is it ?

It will probably all make sense when I actually look tomorrow but my head is hurting thinking about it . LOL

Cheers

 
lots of new wiring req'd. you would need a new cable between light with perm supply(assuming other light is fed from sw live here, and not direct from switch) and switch, and from this switch to middle switch

 
Ignore the earths for the moment...

Intermediate only has 2 x 2 core cables coming in...

2 x 2 way needs at least 2 x 3 core.

do the maths..

you are missing some wires!!!

:_|

 
Ignore the earths for the moment...Intermediate only has 2 x 2 core cables coming in...

2 x 2 way needs at least 2 x 3 core.

do the maths..

you are missing some wires!!!

:_|
Thanks for replies guys. Having slept on it of course some rewiring is needed. Duh :Blushing

Special Location ...The intermediate at the moment will surely have 3 core entering and leaving though won't it ??

Cheers

 
Thanks for replies guys. Having slept on it of course some rewiring is needed. Duh :Blushing Special Location ...The intermediate at the moment will surely have 3 core entering and leaving though won't it ??

Cheers
depends.... if its wired as T&E from light to switch 1, int then 2, then probably. but is swich 1 gets a live, then it may be twin to int and 2 and then single to light

 
Two way ligting circuit wiring diagram

Three way (indtermediate) lighting circuit wiring diagram

Both diagrams (as well as others) are available in download area (larger view).

---------- AUTO MERGE Post added at 13:49 ---------- Previous post was at 13:40 ----------

Ignore the earths for the moment...Intermediate only has 2 x 2 core cables coming in...

2 x 2 way needs at least 2 x 3 core.

do the maths..

you are missing some wires!!!

:_|
Would be interested in seeing a diagram on this one, so I can copy it and add it to our download section, if anyone is interested?

Busy working on the forum upgrade at present. :Salute

 
Would be interested in seeing a diagram on this one, so I can copy it and add it to our download section, if anyone is interested?

Busy working on the forum upgrade at present. :Salute
intermediateswitching.gif


 
Thanks for replies guys. Having slept on it of course some rewiring is needed. Duh :Blushing Special Location ...The intermediate at the moment will surely have 3 core entering and leaving though won't it ??

Cheers
I was relating to just the physical contacts on the switch itself..

quantities of connections..

( as Andy has illustrated )

As you say it is possible that it could be wired taking 2 x 3cores, 7 strapping the 3rd cores though bypassing the actual switch itself.

If it was wired in singles, or a conduit installation it is more possible that only the essential 2 x 2 cores have been taken through the switch.

 
I have been known to take my 3C+E between 2 way switches through the int. switch, and break the strappers across the switch - in which case the fix would be really easy!!!!! (n.b. I always tend to use this method - is it called "method 2" iirc???)

:slap

 
Hi guys

I went rnd and sorted this out today.

As often the case once I was there and got my head rnd it, it was straightforward.

Swapped intermediate for 2g 2w. 3 cores all in position. Just had to run new switch cable in for the kitchen light.

All good.

Cheers

 