- Feb 27, 2008
- 11,015
- 0
So are you saying that all elements unless they are greater than 299mohms are faulty I don't get that. When I did my training 15 years ago I was told not to put cookers, immersion heaters through Rcd's as they have a tendancy to trip them. Since 17th edition I have had to replace countless elements due to them tripping Rcd's they are not faulty just slightly leaky and if it was not for 17th edition they would not have had to be replaced.No, the question was:And I'm not having it that all the items, listed on this thread, leak current to earth - I think this is another myth![]()
I'll give you the computer and some other electronic devices - but not the rest.
If all the items listed leaked between 1 mA and 2 mA in normal operation then you would have to comply with 543.7.1.3 in pretty much every installation you did.
543.7.1.3 The wiring of every final circuit and distribution circuit intended to supply one or more items of equipment, such that the total protective conductor current is likely to exceed 10 mA, shall have a high integrity protective connection complying with one or more of the following:
It then goes on to list 5 requirements - Pg 133 BRB
So, there is no way that those items are going to leak enough current to trip an RCD unless they were actually faulty.
I have an IR tester - thats good enough
Tested my kettle this morning - hot and cold - 500v L & N connected together tested to earth - >299 Mohm
Not a chance of leaking to earth![]()