The breaker is WYLEX 6A 30MA DP TYPE B MINI RCBO
Thanks for your help guys the issue was the inrush current. Changed the breaker with a type C
Back to the op .... do the manufacturers provide any recommendations as the max number per circuit?
do you have test kit?
can you check the zs?
did you check the circuit could take a type C and do any required testing?
Changing a B for a C is an MWC at least.
Thanks for your help guys the issue was the inrush current. Changed the breaker with a type C