doing a few little jobs at a house, looking for the bonding and at the stop cock what looks like a 10mm bond, further investigation the houes lights have no cpc the extention lights have but the last light has its cpc connected to 10mm leading to the incoming water. this is not bonded, but ther is a 6mm coming out of the cu but i dont know were it leads.
going to run 10 mm to the stopcock (pig of a job), so should i connect it to the same clamp as the lights 10mm, they aint going to go for a load more extra work.
they have some new class 1 lights they would like up, should refuse unless class 2 and all the lights and switches in the house are class 1
the zs on the lights is about 2.5
any thoughts thanks
going to run 10 mm to the stopcock (pig of a job), so should i connect it to the same clamp as the lights 10mm, they aint going to go for a load more extra work.
they have some new class 1 lights they would like up, should refuse unless class 2 and all the lights and switches in the house are class 1
the zs on the lights is about 2.5