the test button simulates an earth fault by by-passing one of the transformer windings
Id still like to know where this has came from though.
the test button simulates an earth fault by by-passing one of the transformer windings
so why have you said it creates an imbalance?les,
The test button on an "RCD" only proves the mechanical operation of the device.
There is no more to say.
That is correct.
Steptoe,
An RCD has a current balance transformer inside. The two windings carry line and neutral current respectively. Without a fault these currents are equal and the trani is balanced. In event of earth leakage the current in neutral winding is less than in the line winding so the trani has unbalance and induces current into the trip coil wound on the trani core. This is connected across the trip coil of the breaker and causes a trip current to flow into the trip coil. The breaker trips within 40mS
the post above that you made.Sidewinder,
i'll put it another way.
we need to make sure we use equipment like fuses or CBs that has rated fault capacity greater than the Ipssc measured at that point. agreed?
if this is not the case then the fuse or CB is not able to clear such Ipscc safely without damaging itself and its surroundings. Agreed? so what is not right about this?
Next, I agree that the test button on an RCD only checks the mechanical operation of the breaker.
What is not right about anything relating to this I have said?
Absolute rubbish - the use of an RCD does not obviate the requirement for basic protection - the RCD is there as additional protection in the event that the provision for basic protection fails!I have to disagree with you, Professional. Remember this is not a new job that I or anyone has just installed, but rather it is a 20 year old building that I have taken an interest in as member of the organisation that belongs to the building. Now, in order to add additional protection I added pods to the C-Type breakers. Now a professional engineer agrees with me that as soon as that is done, i.e. an RCD fitted then any/all such circuits need not rely on the CB to clear an earth fault. Now in any job if the correct rating of protective device matches the current rating of the protected cable in that circuit, then no one need be concerned if that overcurrent protective device will protect the circuit from short circuit faults. You are, or one spark replied that he is concerned about testing the L-N loop!!!! Nowhere does any Reg say that this L-N loop has to be tested. It will protect against short circuit faults if it has been rated to suit the size of cable, taking rating factors into account.
The regs do require additional protection now for certain circuits as you know such as where cables are less than 50mm from the surface of plastered walls, and in every socket-outlet circuit, and any type of circuit in bathrooms and other special locations. In these cases this is classed as additional protection, and only the RCD test need be applied but the Schedule of Test Results must be filled in for Zs and R1+R2 and Ze. If Zs is higher than normal for any reason and not your design of installation then fitting an RCD is additional protection BY CHOICE - nout wrong with that, and you will have read that a 30mA RCD is effective with a Zs of up to 1667 Ohms.
Cheers
Why?for Steptoe, please go tohttp://www.tlc-direct.co.uk/Book/5.9.2.htmand read about RCDs